Yes glyptal. Thanks Scotty. Last week I got the two mixed up the other way around.
Rain water is no longer pure, acid rain is common. Acid rain on copper may form copper salts that are corrosive to aluminum. In a distribution system with aluminum conductors running from pole to pole it is common practice to position the copper cable drops from the transformers under the aluminum cables, even though it may look neater to position the copper above the aluminum. Some years ago our little island utility was constructed with the copper drops positioned above the aluminum cables. Corrosion and smoking connections were a chronic issue. A visiting utility engineer gave us a tip and the connetions were changed to position the copper below the aluminum and the issues went away.
In the part of the petro-chemical industry that I am familiar with, copper grounding conductors are run in the cable trays and are connected to the aluminum alloy trays about every 12 meters. The connections are then painted with glyptol paint.
Bras and aluminum, I'm not sure, but if it was my installation I would look for some method to avoid rain or moisture from contacting the brass.
If this is an indoor installation with little likely-hood of condensation or moisture the brass glands will not need protection. (Subject to Scotty's comment re marine or coastal areas.)
Ps Check the locknuts. I have seen issues where aluminum connectors were used with ferrous locknuts. The AHJ demanded that the ferrous locknuts be changed out for non ferrous locknuts.
Bill
--------------------
"Why not the best?"
Jimmy Carter