A further comment to Tip #2
While a moment frame and braced frame in series (i.e. the same column line) probably won't work, in parallel they can. While the differential stiffness may make such an arrangement undesirable, particularly for seismic reasons, sometimes architectural and or industrial layouts do not lend themselves to ideal "bracing" system layouts, and you have to work with what you can use, even when less than ideal. If two parallel bracing lines do not match in stiffness, as long as the centre of reaction matches the centre of load application there should be no torsional loads introduced into the structure. Any inbalance will be handled by a coupling effect of the cross direction bracing system.
Recently I was involved in a project where we actually did mix bracing and moment frames in the same column lines. The structure (tall and skinny) was assembled from a series of modules assembled a thousand miles away from the site. For transportation and erection reasons these modules were assembled as moment frames in both directions (i.e. N-S & E-W). Once erected we were able to install some bracing between certain levels in the longitudinal direction (weaker Y-axis moment frames). This bracing was introduced primarily to provide additional deflection stiffness, but because this bracing was discontinuous, we still required moment frames for the overall structural stability.
The stick diagram below does not fully represent the actual framing, but the general concept. The structure consisted of 8 modules stacked in the following sequence: field erected columns to about 10 ft., then a two level piping module, a single level process equipment module, piping module, process module, piping, process, piping & process. The structure while 52 ft. long, was ONLY 14 ft. wide due to both transportation limitations and plot space limitations within the refinery!
|--------|----|--------|
| |\ /| |
| | \/ | |
|--------|----|--------|
| | /\ | |
| |/ \| |
|--------|----|--------|
| | | |
| | | |
|--------|----|--------|
| |\ /| |
| | \/ | |
|--------|----|--------|
| | /\ | |
| |/ \| |
|--------|----|--------|
| | | |
| | | |
| | | |
---------------------------
While the structure was designed for a seismic zone, we were not able to take advantage of the higher R values that we could have achieved with our ductile moment frames, because we could not tolerate the high lateral sway deflections necessary to mobilize this ductility.
Permissible sway deflections on our tall (88 ft. high) structure could have been as high as 21" under seismic (NBC Canada) code requirements, although while not rated under the Canadian code as a post-disaster structure, as a petrochemical facility similar structures designed under UBC/IBC codes would be rated as high risk, which would have a sway limit of around 10-11". We would have limited ourselves to about 10". Our first pass on our structural model produced deflections in the order of 12" to 14". Piping limitations though restricted us to between 3" & 4", and as a result we ended up with a much stiffer structure that had to be designed for much larger loads, due to the low R value that we had to adopt (our connections were detailed as nominally ductile, but we could never achieve the deflections to actually mobilize this ductility - essentially our structure remains in the elatic region under our design earthquake).