Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Bouyancy of Corrugated Metal Pipe

Status
Not open for further replies.

camdoug

Civil/Environmental
Oct 3, 2002
5
US
What are some calculations that can be used in high water table regions that test situations concerning flotation of storm pipe(namely CMP)? Thanks for the help.
 
Replies continue below

Recommended for you

Weight of the pipe vs. weight of water it replaces and weight of the soil above the pipe. you are an engineer, go for it.
 
I have used the following method to check a pipe for flotation.
The calculation is usually done for a one foot section of pipe.
Forces up equal to the volume of the pipe X the unit weight of water.
Forces down equal the weight of the pipe plus the weight of the prism of
soil over the pipe. For the soil below the water table use a unit weight of
the dry unit of the soil minus the unit weight of the water.( if the pipe is
empty ie. no water flowing in it, the weight of the water in the pipe can not
be counted as part of the force down.)
To keep the pipe from floating the force down needs to exceed the force
up. It is good practice to add a safety factor to this calculation.
 
I agree with AHSmith's approach, except the resisting force should use the SATURATED unit weight minus the unit weight of water. I suppose if the flooding happened immediately, reaching around the pipe before the overlying soil got saturated then maybe use the normal (not dry) unit weight.

Carl
 
Thanks for the responses. I wasn't sure if I should consider it as dunking it into a tub of water or taking the volume of water in the voids of the soil and using the weight of this for the bouyant force.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Top