Dear Mr. KillBill7 (Electrical)(OP)27 Mar 20 20:11
" I am reviewing a structure drawing ......My thinking......the four bolted connections between crossarm and the pole should be enough for the bonding the crossarm and bonding via copper wire is a overkill."
I am of the opinion that:
a) we expect the cross-arm SHALL be properly Earthed,
b) the four bolted connection [may or may NOT] achieve low contact resistance bonding between the cross-arm and the pole, due to painting, surface treatment and corrosion etc., between the contact surfaces. The (structure rigger) would ensure that the four bolts are correctly tightened, but is NOT responsible to ensure [good electrical contact] between the contact surfaces,
c) " bonding via copper wire is " useful to ensure that the contact resistance is maintained to say < 0.01 ohm. The contact resistance should be verified with (four-terminal) measurement method with current NOT lower than 100Adc ,
d) the additional copper wire (very short in length) including the additional connection point on the structure and the cross-arm would cost (nothing) to the project. But it may save life by ensuring the cross-arm is bonded to the structure, which is understood; properly Earthed.
Che Kuan Yau (Singapore)