Bonding ductwork is not done in general practice for commercial work, because there is no hazard from static buildup inside the ductwork. However when handling combustible fumes, or dusts, there is a real hazard from static buildup in the ductwork, especially for non conducting plastic ductwork. Under these conditions one sometimes will make the duct interior static conducting, and will ground that inner liner, or one can run a grounding strap inside the duct to drain off static. On metal duct systems bonding straps may be needed to connect adjacent sections of duct accross the joints, due to the (relatively) high electrical resistance at the joint. Good luck