Our offshore gas platform uses a large number of brass cable glands. The cables are braided armour. The glands are designed to bond the armour. What is the experience of others with respect to bonding these glands to ground? To start the discussion, there are a couple of options being looked at:
1. Use an earthtag (or "banjo" - see to insert over the gland and then run a wire from the earthtag to a grounding stud and from there to platform reference ground.
2. Use a serrated washer and locknut to "cut" into the metallic box and then make sure the box is bonded to the platform reference ground.
The former method is the one that is "recommended" by the vendors but as can be imagined, adds a number of manhours to each box installation. The second method may not have the same guarantee of bonding that the former uses, although both rely on the tightness of the locknut to ensure low resistance in the bonding path.
This discussion is restricted to metallic enclosures only with clearance holes (as opposed to tapered thread hubs).
Comments? Experiences?
1. Use an earthtag (or "banjo" - see to insert over the gland and then run a wire from the earthtag to a grounding stud and from there to platform reference ground.
2. Use a serrated washer and locknut to "cut" into the metallic box and then make sure the box is bonded to the platform reference ground.
The former method is the one that is "recommended" by the vendors but as can be imagined, adds a number of manhours to each box installation. The second method may not have the same guarantee of bonding that the former uses, although both rely on the tightness of the locknut to ensure low resistance in the bonding path.
This discussion is restricted to metallic enclosures only with clearance holes (as opposed to tapered thread hubs).
Comments? Experiences?