Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

bonding of communication tower in substation

Status
Not open for further replies.

hamid66

Electrical
Joined
Jul 14, 2015
Messages
4
Location
IR
Hi
I would like to have some information about bonding of communication tower with main ground grid in electrical substation
in our country (iran) communication tower in substation have separate ground system.
 
Separate grounding systems in a substation greatly increase the possibility of lethal touch and step voltages as a result of a ground fault or of a lightning strike.
While instrumentation and communication people like to have their own ground system our codes require such grounding systems to be solidly connected to the main grounding grid.
This is a life safety issue.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 