I am working on some projects where we'd like to specify turn-of-the-nut method for per-tensioning bolts on some connections between cold form and hot rolled steel.
The cold-form specification is pretty clear that the standard nut rotations from RCSC are not valid due to the small bolt grips due to the thin plies within the connection.
The nut rotations are based on bolt lengths = 4d and 8d and have only been tested on typical hot rolled connection grips (not sure what the typical grips are ???).
My intuition tells me that the issue is that the amount of strain is much higher per a given nut rotation for a short bolt grip vs. a longer bolt grip.
1). Is this the reason the specified rotations in RCSC are not valid?
2). Can testing using a Skidmore Wilhelm still be used to verify the bolt preload with the thinner plies?
My guess is that the required nut rotation for the smaller grip will be less
The cold-form specification is pretty clear that the standard nut rotations from RCSC are not valid due to the small bolt grips due to the thin plies within the connection.
The nut rotations are based on bolt lengths = 4d and 8d and have only been tested on typical hot rolled connection grips (not sure what the typical grips are ???).
My intuition tells me that the issue is that the amount of strain is much higher per a given nut rotation for a short bolt grip vs. a longer bolt grip.
1). Is this the reason the specified rotations in RCSC are not valid?
2). Can testing using a Skidmore Wilhelm still be used to verify the bolt preload with the thinner plies?
My guess is that the required nut rotation for the smaller grip will be less