I thought the OP question was answered adequetely, hence me chiming in with my other question. I'll pose the question as a seperate thread.
On the OP topic, Miller, I don't think it's prudent to have the boiler open into the header and generating steam if you haven't certified the SRV or SRV's that have been overhauled. There is no suitable time frame. Test your SRV's FIRST. Production requirements are secondary to safety.
Let me ask a different question then to all folks. What is the practice at your plants regarding "floating safety valves" (popping them) on the boiler to certify set point and blow down? Do you routinely do this? Don't do it? What are you talking about? Trevi test instead? ???
There's a push at my plant to not float boiler SRVs because it's a noisy process and can damage the SRV seats. However, the number of times I've seen a different pop pressure on the boiler as opposed to the one on the bench - both above AND below the bench figure, says to me that "on boiler testing" prior to steam production is a must.
- - - - - - - - - - - - - - -