I suspect this is a scotch marine fire tube type boiler or something similar.
Many of these type boilers come std with dual controls, one set for 150 psig, and another for 15. Some boilers are designed and stamped for 150, and sold and operated at 15 psig. I don't see a problem here if the boiler was originally designed (nozzle outlet sizes, etc.) for the lower pressure.
YOu do not say if you had other users, although a 6" header makes me believe you might. Others have run the math on the velocities, and I am not going to check them, but I agree with the choked flow conclusion above, and believe that your header was not operating at 15 psig, while your boiler might have well been.
If I am right about that, at a reduced header pressure, the other users that may have been previously "starved" for sufficient steam flow, are now satisfied, and are pulling more steam than before, "bullying" if you will, for lack of a better technical term, the kettles.
Alternatively, if other users are not the culprit, then your traps are suspect, as now that the kettles can get all the steam they want, they may be flooding the traps that weren't 'pushed' before when the kettles were somewhat starved for adequate steam supply.
rmw