POPPASMURFF1942
Petroleum
- Nov 2, 2006
- 11
Good morning Gentlemen and Ladies. The problem is I have a 100K pph natural gas boiler that will only turn down 2 to 1. The problem stems from the fact that at the lower rates the pressure in the fire box/furnace area swings from +2.9 wc to -1.2 wc at 50K pph. At 40K pph the swing get worse +2 to -3.6 WC. The burner and fuel gas pressures are very stable. The wind box pressure swings a little due to the furnace pressures swinging. Now this is where I am looking for expertise. This boiler has a 72" stack that is only 8 feet tall. What I am thinking is that if the stack were much taller with a conical top swages in to 48" diameter or a Cooley hat top that would not allow back flow would solve my problem. Any thoughts, sizes or recommendations.