NFPA rules may require the boiler be purged with air to remove combustibles for 15 minutes .
Following an MFT ( master fuel trip) and loss of fans, unburned coal or other fuel lies smoldering on the furnace hopper , generating CO. Unpurged NH3 nozzles in the SCR pass may also be leaking NH3 to the convection pass. Persons cannot access the boiler unless one is certain the CO and NH3 is removed.
Another recent need for a fan purge is related to the use of wet FGD systems- they have an effective water seal of about 0.5 in WC ( additive to the gas frictonal pressure drop) whenever the A/R pumps are running, and this prevents "natural draft" from occurring on hot days ( combination of low stack gas temp , low stack, hot ambient temps, and 0.5" WC water seal acrosss the absorber trays). So one needs to use the fan to get a purge.