After checking the ASME PTC4 Power Test Code for Fired Steam Boilers I could not found boiler feed water system balancing procedures.
How should the boiler feed water system be adjusted or balanced to prevent overflow pump conditions?
How to account for delivering proper minimums flows to all boiler feed water valves without overflowing the closer boiler and giving less flow to the farther boiler?
Should a balance valve be throttled before the feed water valve of each boiler to equalize all the boiler pressure drops at full load conditions?
Should this be done with a dummy steam load at start up, or could it be done by pressurizing the boiler before first firing and use cold water only and letting water to flow back to the deaerators?
For example, everybody says to install an orifice or bypass valve at pump discharge to account for dead headed situations. But what about the overflow possibility of a feed water pump?
If for some reason you have three boilers been supplied from two feed water pumps in a common header. The closer boiler will receive more available pressure and flow than the farther boiler when all the feed water valves start opening. Still during the boiler start up almost never will the load be available at the building to simulate the worst case scenario of a 100% load. So the start up is done with the boiler plant at less than full load capacity and the feed water pumps pressure is not equally balanced between boilers.
This procedure should be part of a standard or code to make sure the boiler plants are tested at full load conditions.