Thanks for your answer, however I don't think my original question was clear enough. Working back from the boiler towards the feed pumps, B31.1 122.1.7(B.1) requires a stop valve closest to the boiler, and then a check valve. On a boiler I've seen, the line was arranged with a stop valve at the boiler, and then a stop check valve closer to the feed pumps. In accordance with the code, para. 122.1.7(B.6), this stop check valve only counts as a stop valve, and to be compliant the boiler would require an additional check valve to be installed. So... why is a combination stop check valve considered only to act as a stop valve. Why can no credit be taken for the "check" function of the valve.