Block Piers Filled cells with mortar but no mortar in bed joints- what is their strength? 2

Status
Not open for further replies.

ajk1

Structural
Apr 22, 2011
1,791
I am reviewing some aspects of a cottage that has been built in the last year. I had nothing to do with its design or construction. To avoid putting in a pump for the septic tank, the cottage was built so it is raised up, sitting on concrete block piers. The land slopes, so the piers vary from 1 block high to 7 blocks high. Each pier block is 10" x 16".

All piers sit on rock according to the contractor. The piers were built with no mortar in the bed joints, but the contractor says that the cells were filled with mortar (although drilling a hole into each of 3 piers seemed to indicate void in one pier and solid in 2 other piers -- I have not been to the site to see -- the contractor refused to drill the 5 exploratory holes I requested, saying 3 was enough. There are 11 piers under the cottage).

Construction photos show that there are 2-15M dowels per pier, and that they extend about roughly 4 to 6" up into the bottom block from the concrete base below. The contractor says that there is no other rebar in the piers.


QUESTIONS


How to check the structural adequacy of the piers to resist the wind lod on the cottage and carry it down to the footing?

I have tried two methods, as follows:

Method 1: Check the maximum horizontal force that can be applied to each pier, based on a saftey factor of 1.65 against overturning. Sum this load for all piers, and compare it to the wind load acting on the cottage, in each direction. If it is less, then there is no chance of the piers having adequate resistance against the wind, and determining how much wind load goes to each pier (by computer modeling) is unnecessary.

Method 2: Similar to methiod 1, except base it on stresses in the grout, using only the grout in the cells and the Code allowable stress for grout (if I can find that). Perhaps I could take the face shell on the cmpressive side of the block as working with the grout in the cell, in carrying out this check.

Both of these methods seem to indicate the piers are inadequate (based on 30 psi allowable tensile stress in the grout in Method 2, although perhaps I could use a higher stress).

Any comment?

 
Replies continue below

Recommended for you

I was the one who commented on the additional mass comment. I mistakenly assumed (must have been cooked) that he was considering the mass as a way of adding inertia to the system to resist wind. (I guess I though that because technically, mass is not a measure of weight even though they seem to be used interchangeably on earth).
 
ajk1,

Strengthening the existing piers by wrapping with carbon fiber or concrete is ineffective if the footings are incapable of developing enough resisting moment.

In my opinion, a much better way to achieve lateral stability is to build four short shear walls, one on each perimeter wall. Each shear wall should be tied to at least one existing pier (preferably two). Together, the shear walls would carry all of the wind, leaving the existing piers to carry only gravity load.