I have a project that has a depressed area on elevated composite structural steel framing. We kept the same slab depth throughout and depressed the steel in the bay with the depressed slab. While the shear stud installer was going through the project, he switched out longer studs on the fly in the depressed area and now the studs will stick out above the proposed slab elevation.
My question is:
Can the contractor bend the studs over slightly so the top of the stud meets the clear cover requirements? If any break off during bending, he will install the proper length stud in its place. Based on composite design and shear flow requirements, I don't see how the orientation or bend in the shear stud would impact the stud capacity. Thoughts?
My question is:
Can the contractor bend the studs over slightly so the top of the stud meets the clear cover requirements? If any break off during bending, he will install the proper length stud in its place. Based on composite design and shear flow requirements, I don't see how the orientation or bend in the shear stud would impact the stud capacity. Thoughts?