I have an application where I need to install some Belden or equivalent mulit conductor cable in a cable tray. One of the cables I want to use is an 8760. This tray will be located outside. Is it acceptable to use these cables in a tray?

TIA.
 
Replies continue below

Recommended for you

I doubt it. You need UL labeled type TC cable, listed for use in cable tray. I think Belden may make some TC cable, but I'm not sure these days.

Check with Okonite, or do a Google search for the type of cable you need.
 
Take look at Belden 9318. That should be a #18 shielded twisted pair Power Limited Tray Cable.
Don
 
Thanks, I think that will work.
 