I am designing a 4,000 sf office area wholly contained inside a 10,000 square foot building. Thee office is a big box 40'x 100'. The perimeter walls will support ceiling joists only. There is a clear space between the office ceiling and the warehouse roof of around 14 feet. My questions are:

Would you design the ceiling joists for 10 PSF or 20 PSF live load?

Would you consider the walls supporting the ceiling joists to need a footing (ie saw cutting slab to provide 12" deep footing or can the wall just attach to the slab. I could check the slab for shear and I think it will probably work). The max load along a wall will be around 500plf. The slab is 5" thick, but I don't know what kind of reinforcing it has?

PS. The building within a building will be designed for seismic loads and footings will be provided at shear walls.

Thanks in advance for your opinions.
 
Replies continue below

Recommended for you

If those ceiling joists shield a space for mechanical ducting, electrical, etc. where a workman can access in the future for remodels, use 20 psf live load. If not, use 10 psf.

Mike McCann
MMC Engineering

 
Thanks msquared48 I appreciate the advice. They are supporting some mechanical equipment and I will use the 20psf.
 
I've seen spaces like that become very tempting for storage.
 
I was worried about that too. I emailed the client and put the email in my file... They said it wouldn't be used for storage.
 
Doesn't the geotechnical report specify what uniform load is OK for a slab w/o footing? Ask for an addendum.
 
They don't have a geotech report. The existing warehouse was built back in the 60's.
 
If the soil is reasonably competent (enough sand content) I don't see a problem with 500 plf.
 
Thanks for the input AELLC!
 
I would use 20 PSF ceiling load and 5 PSF minimum lateral load on each wall for stability. I would put the bearing walls on footings even if the numbers worked out to bear it on the slab.
 
500 plf should not be a problem on most slabs. I usually jump on the slab or hit it with a hammer. If it sounds hollow underneath, it means some settlement of the subgrade has occurred and the capacity may be questionable. I believe slabs-on-grade on decent subgrade have significantly more capacity than we give them credit for.
 
Even though the loads are pretty light, I would want to inspect the slab exactly where the walls are going and have a chance to address cracks and joints (fill with epoxy). I would probably drill a few holes in the slab and probe with a CPT to see what the soil looks like. It may be overkill, but fast and cheap insurance just to know what is under the slab.

However, compared to a rack or forklift, those are light loads. And 500plf is presumably with a full live load, which that roof will never see, and most of its life there will be next to zero live load.

Agree with Triangled, this roof looks like a mezzanine and someone will want to stack crap up there. At a minimum I would put your live load very clearly on the drawings and indicate this is not designed for storage.
 