The general bearing capacity equation can be simplified into nine equations. Three each for granular soils(phi soils), cohesive soils(C soils) and mixed soils (C-Phi soils).
The three equations in each soil type depend on the shapes-continuous, square/rectangular, or circular. For illustration, let us assume we have mixed soils, i.e with phi angle and cohesion. Since you have strip footings, our equation would reduce to the Terzaghi bearing capacity equation for the general shear case or CNc + Gamma*D*Nq * 0.5*Gamma*B*Ngamma
By that equation, if width of Strip B and Strip A are the same, then we have the exact ultimate bearing capacity. However, if we examine, Strip A, the log spiral is confined on the excavation side, so intuitively we should get higher bearing capacity. By how much is obtained, that is hard to tell. But regardless, that ultimate bearing capacity is divided by 3 to obtain allowable bearing capacity. This division dilutes any prior side excavation advantage. As oldestguy pointd out, that allowable would further need to be reduced to limit settlement to 1 inch or so.
In your 3rd post, point 2)you mentioned uplift resistance. There is heave and there is uplift. Heave is common in cohesive soils, when deep excavations are made. Uplift can be caused by cohesive soils upon wetting, particularly by expansive soils or by GWT close to the bottom of the basement. Instead of just checking depth*gamma, we look to see if :
Uplift pressure < 0.5 allowable bearing capacity &
Uplift pressure < downward pressure form foundation loads
If both cases are true, and you have no expansive soils or ground water conditions, then uplift pressure is not a concern.
Sorry to be lengthy, but let us try to clear somethings. We will have a different scenario if you had a trench. Depth would be the same, but we could take advantage of side wall friction on both sides to obtain bearing capacity.
For settlement, we pick an allowable bearing value, width B, and averaged percent strain for 4B below the footing, and plug that into an equation. If the ouput is high, then we reduce allowable bearing pressure and/or increase B and rework until we get acceptable settlement.
We are only partially done- total settlement does not govern, differential settlement controls.
So we check to see that all the footings are settling by similar magnitude or we have a difference less than L/300.
Differential settlement calculations is where you need the geotechnical engineer-that is another post.