hp48sx
Civil/Environmental
- Mar 13, 2008
- 4
Good evening,
I have a question about an application of a bearing pad. We have an application where a 24” ball valve in a pump station is mounted to a concrete pedestal. The ball valve is located “in-line” between a large pump and a pipe header distribution system. We are suppose to use a bearing pad and limit the compressive stress on the pad to no more than 12 psi.
Based on the Dead load of the valve assembly and the some contributory load of the surrounding appurtenances (15,100 lbs) I have calculated a required minimum baseplate and pad size of 36” x 36” square (11.65 psi).
The engineer is now telling me that there is a startup pressure on the closed valve of 61 psi – this pressure is relieved as the valve is opened and the pump continues to run. He says that an overturning moment is induced in the valve base support and thus creates an additional compressive force on the bearing pad. With a calculated approximate force of 27,500 lbs on the closed valve (61 psi x area of a 24” dia pipe) and a moment arm from the top of the support to the centerline of the load equal to 29.5 inches, the design “blows up” and a bearing pad could never work.
It seems to me that any horizontal force applied to the closed valve would first go into the surrounding pipe and pump supports before it is transmitted through the valve bearing pad and into the valve support.
What guidance can you give me to help me limit the applied stress in the bearing pad to 12 psi?
Is it even reasonable to limit the stress in the pad to 12 psi in such an application?
Thanks in advance for your help.
I have a question about an application of a bearing pad. We have an application where a 24” ball valve in a pump station is mounted to a concrete pedestal. The ball valve is located “in-line” between a large pump and a pipe header distribution system. We are suppose to use a bearing pad and limit the compressive stress on the pad to no more than 12 psi.
Based on the Dead load of the valve assembly and the some contributory load of the surrounding appurtenances (15,100 lbs) I have calculated a required minimum baseplate and pad size of 36” x 36” square (11.65 psi).
The engineer is now telling me that there is a startup pressure on the closed valve of 61 psi – this pressure is relieved as the valve is opened and the pump continues to run. He says that an overturning moment is induced in the valve base support and thus creates an additional compressive force on the bearing pad. With a calculated approximate force of 27,500 lbs on the closed valve (61 psi x area of a 24” dia pipe) and a moment arm from the top of the support to the centerline of the load equal to 29.5 inches, the design “blows up” and a bearing pad could never work.
It seems to me that any horizontal force applied to the closed valve would first go into the surrounding pipe and pump supports before it is transmitted through the valve bearing pad and into the valve support.
What guidance can you give me to help me limit the applied stress in the bearing pad to 12 psi?
Is it even reasonable to limit the stress in the pad to 12 psi in such an application?
Thanks in advance for your help.