smcgee,
I've got a few comments. You're absolutely right that you need to have those things before you can make a bearing capacity determination. Look all through the report and see if they don't make some good assumptions (or even knowns) regarding the type of structure, loads, usage, footing type, etc. They should know those things before they develop recommendations. It is very dangerous to say a site has a "bearing capacity" of 2,000psf without knowing what is planned, because that value is highly dependant on what is being built there. There also may be more than a single recommended bearing capacity for a structure too. Maybe for different structural elements or something.
Also keep in mind that the "bearing capacity" value you see (if that's what they call it) in the report is actually a misnomer since the value you're reading is actually an "allowable bearing pressure" figure. See what I mean? The allowable pressure given may be limited by settlement, not an actual shear failure of the soil. For example, the bearing capacity of a given footing on a given site with given loadings might be 8,000psf, whereas your soil contact pressure to limit settlement to an acceptable value may be 2,000psf. Clearly, you can only apply 2,000psf since settlement controls. It is also possible to have instances where bearing capacity (soil failure) may control the recommendations rather than settlement too.