Beam connection stability 7
Vrpps EIT
58
Hi All,
Attached the situation in the pic, under this loading, when the overhang portion has a column on top of it and has a point load. This creates a moment at the beam and column-A connection. which in turn will create an uplift load. So, this uplift will be resisted by the beam & column-B connection at end of the beam which is fixed there or the four bolts that are connected at beam column-A connection? Or in simple terms what tensile force should the 4 bolts at column support A near the overhang to be checked for is it the reaction force that support will carry?
I can see it as a tower crane with balancing counter jib but I am missing something here.
Thank you for your time!
 https://files.engineering.com/getfile.aspx?folder=2e3d4853-5d88-4ea1-a52b-861a35338f7a&file=Scan001_(5).jpg
I just did a quick check, if the moment in the column is around 1 ft-k, the code specified minimum will cover (with e=b/6, b=5").
2-D verifications (W10x30 Beam, HSS5x5x3/16 Column):
Pinned Beam-Column Joint
Rigid Beam-Column Joint
retired13- What is the software in the above image?
RISA 2D. You can download free trail.
The load at the end of the cantilever is applied by a HSS column. Everyone so far seems to be regarding its connection with the beam as a perfect pin when in fact it cannot be. If that HSS is rigidly connected to the beam, it too must take moment, for which it should be designed. Also, the moment taken by the end column reduces the cantilever moment.
Is there a valid reason to be so concerned with one connection while completely ignoring another?
BA
BAretired - is this really true? Usually the moment in a cantilever is entirely independent of the assembly beyond (behind) the cantilever right?
In this case, the cantilever moment is always P x (Cantilever Length).
retired 13, what is the rotation of the beam at the column in your pinned example?
JAE,
The end column will reduce the cantilever moment if the slope is as shown in retired13's Risa 2D output. If the span moment is dominant, i.e. if it creates an upward slope in the cantilever, then the end column will increase the cantilever moment. In the special case where the slope is zero as a result of the simultaneous span and cantilever loading, the end column stiffness will have no effect on the cantilever moment.
BA
Rabbit12,
Here is the deflection table. Beam L-R jt 1-3, column base jt 4
BA - when you say "end column" are you talking about the column at the end of the cantilever?
For the rigid connection model,
Yes JAE, I'm saying the end column is the column at the end of the cantilever.
EDIT: All of a sudden, I am realizing that you thought I meant the column at the end of the span. Of course, that column would have no effect on the cantilever moment.
BA
And so assuming that the end column is "fixed" to the cantilever, then yes, the cantilever moment might be affected by relative stiffenesses.
Got it thanks
In my experience the simple snug tight bolted cleat connections exhibit more rotation and less stiffness than axially loaded cap plate connections. Though I would be happy to be proven wrong and I believe it will make an interesting discussion. If anybody has research on this I am listing.
**One thing to note that sometimes a rigid connection on a column can actually REDUCE the applied moment to the column compared to a typical eccentric cleated connection. This of course depends on the eccentricity, the loads and the members involved.
Are you saying the column should be designed for the moment, or the connection?
Definitely. A cleat plate is much closer to a pin than a cap plate. The bolts are in bearing with slop in the holes, and the cleat itself is a lot less stiff than the member.
In practice, it is usually beneficial if you can use simple bolted connection. However, the column inevitably will experience some moment due to rotation of the beam against the edge of cap plate. Therefore, it is advisable to design the beam for the full moment, and design the column with a moment equal to P*bp/2, bp is the width of the cap plate.
The connection is intended to be a pin, but some moment transfer is inevitable. The column at the end of the cantilever should be designed with that moment in mind.
BA
There has been no mention of "simple snug tight bolted cleat connections". The OP's sketch indicates an HSS column at the end of the cantilever with no description of its connection to the beam. There is no indication of the load on that upper column, so it is possible that a cap base plate would be needed, not to mention a stiffener under one or both walls of the HSS.
It is inconsistent to quibble about ignoring the moment on the lower column while happily ignoring the moment on the upper column. How could you be proven wrong and how could anyone have research on something as ethereal as this?
BA
BA,
Do you mean there is a HSS column on the tip of the cantilever?