stevenal
- Aug 20, 2001
- 3,855
A thread a while back strayed into the subject of testing BCT polarity while installed on a power transformer. I cannot find the thread anymore. Red flagged for some reason? Anyway, I mentioned performing such a test a few years back and claimed I didn't remember shorting the unused power transformer windings. I had occasion to do a similar test this past week, and the instructions were clear that the unused power transformer windings were to be shorted. The test set involved is a Multi-Amp ratio, excitation and polarity tester. I believe Multi-Amp is now Megger. The set applies a voltage to the CT secondary, and displays the primary voltage added to or subtracted from a fraction of the secondary voltage. When switched from add to subtract, reading will drop if polarity is correct and increase if reversed. We were able to quickly correct a REF protection scheme, and increase our confidence in a bus differential scheme.
Just wanted to clear up any misunderstanding I may have caused.