NickParker
Electrical
- Sep 1, 2017
- 446
I have 9 Strings of Battery bank (35 cells per bank)
6 strings are connected in series to get a voltage of 476V (As an input to the UPS Inverter).
3 strings are connected in parallel to support the loads for a longer time.
9 x 35 = 315 Cells (Total number of cells including the series and parallel connected)
6 x 35 = 210 Cells (Series connected cells which produces a voltage of 476V)
Which one (315 Cells or 210 Cells) should I consider in the below equation (for "No. of cells")? The battery banks have been purchased. Now that loads/Autonomy have been increased, would like to check if the Battery AH is sufficient or not?
6 strings are connected in series to get a voltage of 476V (As an input to the UPS Inverter).
3 strings are connected in parallel to support the loads for a longer time.
9 x 35 = 315 Cells (Total number of cells including the series and parallel connected)
6 x 35 = 210 Cells (Series connected cells which produces a voltage of 476V)
Which one (315 Cells or 210 Cells) should I consider in the below equation (for "No. of cells")? The battery banks have been purchased. Now that loads/Autonomy have been increased, would like to check if the Battery AH is sufficient or not?
