Don't forget to consider that the horizontal load creating the bending moment may be applied in a diagonal direction. If applicable, this load direction will almost certainly control the design of the anchors and base plate and may also control the design of the footing if the footing is limited by soil bearing stress rather than overturning.
Regardless of the direction of the load, the first step would be to calculate the anchor bolt axial forces. This will require that you determine an appropriate location for the center of compression. If the base plate is grouted, that can be a challenge, but it's probably near the edge of the column. If the base plate is held up on leveling nuts, then the compression load travels through the anchors and it's a much simpler problem. As HotRod10 stated, you can design the base plate as a cantilever transferring the bolt tension (and compression if applicable) back to the column. The cantilever length is the shortest distance from the anchor center to the nearest face or corner of the column. The effective width of the cantilever plate element is usually taken as 2 times the cantilever length, but should be truncated if the effective widths of adjacent anchors overlap or if the effective width extends outside of the physical edges of the plate.