The anchor rods for a column were supposed to be set in a 1'-4" square pattern, but instead they were set in a 1'-2" square pattern. The column is part of a moment frame. It is a W10x112, the base plate is 2" thick with 2-5/16" diameter holes, and the anchor rods are 1-1/2" diameter with 3-1/2"x3-1/2"x1/2" plate washers. I have checked the plate thickness and anchor rod capacity for the effect of the anchor rods in the in-situ locations and the plate thickness, anchor rod tensile strength, and concrete break out strength are all ok. There appears to be just barely room to fit the specified washers over the in-situ anchor rods and clear the corner of the wide flange section. So, I would like to use the anchor rods in the in-situ locations.
My question is how to go about modifying the base plate to fit on the in-situ anchor rods. I have attached a detail of the original base plate and anchor rod layout with the actual in-situ location of one of the anchor rods also shown (top left anchor rod, but the other 3 are similarly offset toward the center from the specified locations). Is it OK to slot the existing base plate holes, or should I specify that the holes be filled and new holes drilled. There is a recommended procedure in AWS D1.1 5.26.5 and C5.26.5 for filling the holes. One of my concerns with slotting the existing base plate holes would be that I guess the plate washers would have to span the gap over the slotted holes.
