calvinandhobbes10
Structural
- Feb 14, 2011
- 106
First Eng-Tips post. Visited these forums for years.
Steel truss vibration problem. We use DG11 and FloorVibe.
We have a conference center that features a grand ballroom over another smaller ballroom space.
6-ft deep steel trusses span 81 feet over the small ballroom, and support the grand ballroom floor.
The max trib to a truss is 31 ft. All the trib area is part of the ballroom.
6 1/2" normal weight floor slab (2" deck + 4 1/2") floor, with composite beams framing to the trusses.
We're designing for dining/dancing vibration, 2.0%g limit.
Truss depth is set.
I used FloorVibe (knowing that trusses may be a different animal) to ballpark this truss, especially its frequency.
Used 81' x 31' bay. In the program, trusses are User-Defined shape, using 0.85 * Ig(chords) and Area(chords) to approximate the trusses.
Truss natural frequency as-is comes in around 5.3 Hz, the whole bay around 4.8 Hz.
My questions:
1) I'd expect an additional damping or diffusing mechanism kicks in when you are looking at a larger tributary area (that won't ever see full dancing), but I'm not familiar enough to know how this might be applied. My question 2 is my best-guess. Does anyone know of anything like this? I.e, difference between ten and three hundred people doing the cupid shuffle--there's certainly a break point below which the sensitive occupancy doesn't feel it.
2) Can a form of live-load reduction be applied to vibration? My hypothesis is that I can reduce wp, weight of participants, same as live load (by up to 50%), which reduces the applied acceleration accordingly. DG11 provides 12.5 psf, FloorVibe suggests 6 to 12.5 psf. I take 12.5 (DG11) and apply an analogous live load reduction.
3) Is FloorVibe reasonably accurate to approximate a steel-truss frequency? We have not done an FE model for this. We verified our moment of inertia with our actual truss design (Ram Elements) and I don't really suspect an FE model will end up being that much different.
4) Adjusting the truss to meet the acceleration limit in FloorVibe (using my 6.25 psf live load from question 2), at first check yields a truss about three times the moment of inertia required by gravity. Is this expected or normal for an application like this?
5) The truss top and bottom chord will be horizontally braced. Disbursement cross-bracing is normally just a retrofit option for joist vibration issues, but does this have any effect on design calcs? Doesn't show up in DG11 but am curious if anyone knows much about the effects. FE model might be the only way for this.
We are under pressure to keep steel tonnage in a tight budget and don't want to beef up the trusses unless we absolutely have to. Deepening the trusses or adding more of them would be my next recourse.
Appreciate any insight.
David
Steel truss vibration problem. We use DG11 and FloorVibe.
We have a conference center that features a grand ballroom over another smaller ballroom space.
6-ft deep steel trusses span 81 feet over the small ballroom, and support the grand ballroom floor.
The max trib to a truss is 31 ft. All the trib area is part of the ballroom.
6 1/2" normal weight floor slab (2" deck + 4 1/2") floor, with composite beams framing to the trusses.
We're designing for dining/dancing vibration, 2.0%g limit.
Truss depth is set.
I used FloorVibe (knowing that trusses may be a different animal) to ballpark this truss, especially its frequency.
Used 81' x 31' bay. In the program, trusses are User-Defined shape, using 0.85 * Ig(chords) and Area(chords) to approximate the trusses.
Truss natural frequency as-is comes in around 5.3 Hz, the whole bay around 4.8 Hz.
My questions:
1) I'd expect an additional damping or diffusing mechanism kicks in when you are looking at a larger tributary area (that won't ever see full dancing), but I'm not familiar enough to know how this might be applied. My question 2 is my best-guess. Does anyone know of anything like this? I.e, difference between ten and three hundred people doing the cupid shuffle--there's certainly a break point below which the sensitive occupancy doesn't feel it.
2) Can a form of live-load reduction be applied to vibration? My hypothesis is that I can reduce wp, weight of participants, same as live load (by up to 50%), which reduces the applied acceleration accordingly. DG11 provides 12.5 psf, FloorVibe suggests 6 to 12.5 psf. I take 12.5 (DG11) and apply an analogous live load reduction.
3) Is FloorVibe reasonably accurate to approximate a steel-truss frequency? We have not done an FE model for this. We verified our moment of inertia with our actual truss design (Ram Elements) and I don't really suspect an FE model will end up being that much different.
4) Adjusting the truss to meet the acceleration limit in FloorVibe (using my 6.25 psf live load from question 2), at first check yields a truss about three times the moment of inertia required by gravity. Is this expected or normal for an application like this?
5) The truss top and bottom chord will be horizontally braced. Disbursement cross-bracing is normally just a retrofit option for joist vibration issues, but does this have any effect on design calcs? Doesn't show up in DG11 but am curious if anyone knows much about the effects. FE model might be the only way for this.
We are under pressure to keep steel tonnage in a tight budget and don't want to beef up the trusses unless we absolutely have to. Deepening the trusses or adding more of them would be my next recourse.
Appreciate any insight.
David