I originally tried a glulam in the center, but it WAS overloaded. Utilizing (2)glulam's I have quite a bit of capacity. I thought the load would be more than it is, but when accounting for tributary areas and 14psf wall wind loading, I only have about 1400 lbs total point load on the column. Deflection isn't the best, but my calc is a little conservative so I'm not too concerned about it.
I have in my red-line notes that full height LSL's are an option in lieu of the Glulam detail. I just think the Glulam detail with a double 2x8 (went with 2x8s to keep uniformity for the wall framing as the wall width is now governed by the glulam width) will be a lot less headache on the contractor for a few reasons: 1) LSL's are a pain to nail into, 2) it's fitting (2)-sticks of lumber full height instead of a bunch, 3) once the glulams are in place, the framers can frame just as usual and not have to worry so much about a very flemsy tall wall, 4) I don't know how much a stick of LSL costs these days but traditionally it has been much more expensive than DF.