Okieduck,
You clarified a point that has been bothering me about your original thread. Up here where it is somewhat cooler, many backflow preventers are installed within the building or compound themselves, versus a vault or similar structure. Along with that, usually the meter is within proximity and therefore access is not usually an issue.
I must reiterate my initial response however. Is backflow prevention a criteria developed by the municipality to protect the water distribution system from contamination, or is it a warm and fuzzy get to feel good project for new developments and services? I ask because unless backflow prevention is systatically implemented and integrated in the distribution system it is not very effective and proven to be a wee bit of a burden on already strained budgets. Case in point, two commercial buildings (allowing a variety of uses), one constructed 20 years ago, the other approved for construction by the municipality. The newer building has backflow prevention by statute, the other is grandfathered. How is the system protected if the system goes into draw (vacuum)?
I have personally experienced and entire system go into vacuum (reverse pressure) affecting a town of 2,800 people. I too was a big believer in backflow prevention until this incident. We were very lucky that contamination of the system was not reported and the entire system was immediately flushed. Case in point, the only way to prevent widespread contamination was to isolate the distribution system. Had backflow preventers been installed on each and every service, and proven to be in good working order, the risk of contaminatin would have been dramatically reduced however, the resulting actions by my staff would have been the same. So in the end, could your City respond to an event like we did, and given your present backflow prevention program, would it really make a difference?
In additon to the other considerations raised by the other threads, you must also look at public safety and how it is best being served diligently.
Incidently, I recieved unanimous funding to install numerous additional "emergency" isolation valves throughout the system and complex monitoring devices as a response to that event ever occuring again.
KRS Services