Not a problem Cher,
I would recommend that you do your homework and ensure that the 12" service is sufficient. This can be either via a hydraulic study prepared by a separate consultant or even just a quick rough model that you develop to determine you are delivering sufficient flow and pressure to the site.
In response to your first question, this is what I meant by needing more information about your site. For example, a 12 inch service is once again as I mention a large fire service, so I don't know if you are responsible for only the service up to the DCV or are you preparing an entire underground fire delivery system onsite. Without making too many assumptions on my side and based on what you mentioned, you would potentially need additional check valves if the length of your service from the DCV to the fire department connection is too long. What is too long? It would be the length determined by either your hydraulic calculations and/or your coordination with the fire department. You may find out that the FDC is 200 ft from the DCV and when the fire truck connects to the FDC, now the pumper truck is trying to push water both into the building with some loss pushing back towards the DCV. There is nothing magical about the 200 ft number that I mentioned, this is just a number.
With respect to the DCV, you are correct to start with the local jurisdiction. In fact in many of the installations that I have done, the local agency will own the water service from the main to the right of way, just before the DCV. While they do not own the DCV, they do dictate which model is allowed. A few items to note, check on their detail. Sometimes their detail is too generic so you will need to ask them more questions. For example some agencies have an already approved list of DCVs already on file. Another question to ask, is if the pressures in the main are high enough or additional requirements that may call for the need of a reduced pressure principle as part of the DCV? Some agencies make this a requirement for additional protection to their system. If an RP component is required, you will need to provide some sort of splash box directly below it since water will drip from this unit. Manufactures such as watts, wilkins, febco and others have information on the different models, as well as CAD drawings that you can use for both vertical and horizontal placement. A 12" DVC device will have a good size footprint so many times the the agency standard is not enough to place these onsite.