Hi snorkles;
There is one point of your contingency plan that I am concerned about.
You may have a probem energising the transformer at the generator location. If so, close the breaker to the transformer and bring the generator and the transformer up together. Depending on your exitation scheme you may do this by just starting the gen set with the breaker closed, or you may start the generator and then energise the field.
You may even connect cables directly from the generator to the transformer. You may have to jumper or disable some trips.
This is not my main concern.
My main concern is the other transformers and transformer banks on the 12,470 volt system. If all your transformers have delta primaries there should be no problem. There are however, problems feeding a wye primary transformer from a delta system.
Hence my questions earlier as to the configuration of your system and the availability of spare transformers.
We are glad to help with your plans and you can backfeed in principal but there may be a few technical issues to consider.
Another question, does your 12,470 volt distribution system include a neutral conductor or just three phase conductors?
How much of your 4000 KW capacity would you be backfeeding in an emergency?
In responce to the valid concerns that some posters have expressed as to issues with the utility company:
I was involved with the emergency response and temporary measures following a hurricane that wiped out virtually an entire small utility. (Very small). The very few wood poles that were not broken by the hurricane were suspect and replaced. 100% of the wood poles were replaced.
At one plant, we were backfeeding the plant from the on-board generator of a ship moored alongside. Another plant located a new generator and had it rushed in.
A contractor from a neighbouring island sent in a crew of volunteer electricians and an old gen-set, and they quickly rigged up temporary street lights for the security of the community. After a month or so, the old genset failed. I was going for lunch and one of the community leaders approached me and asked what options were available to restore the security lighting for the community. We found the manager of the local utility. We were heading to the local seafood plant (where we had previously installed the generator) to consult with the manager/owner and met him going for lunch. The need for lighting was accepted. With my assurances that the plant had a transformer with adequate capacity and the proper voltage, the plant owner gave permission to feed the lighting from the sea-food plant generator. This street corner meeting took about 5 minutes. I was given a small crew and before dark we had power back on the street lights. The system was used for 3 or 4 months until the regular utility system was rebuilt.
The point is, in a serious hurricane emergency, the utility is usually very happy to see a large customer cut themselves free and fend for themselves. It takes a lot of pressure off the utility. snorkles may find himself aproached by the utility with a reqest to backfeed a nearby critical load such as a clinic or small hospital.
respectfully