MotorCity said:
...assuming you can convince yourself that a joist can serve as a rigid support in its weak axis...haha.
Why weak axis? I only see the joists being worked in strong axis flexure for this.
MotorCity said:
Hopefully no code writers are tracking this thread and jumping for joy at the possibility of adding 30 more pages to require a check like this.
I'm in the minority in that I'd actually prefer for there to be more prescriptive requirements in the code so as to make it easier for designers to make smart choices rather than racing one another to the bottom. If I had my way, there would be one line in both he IBC and IRC that said:
All floors at and below grade shall be constructed of CIP concrete not less than 6" thick unless a discrete, horizontal bracing system is provided in liu.
Boiler106 said:
how about rather than taking the compression through the deck, you design the deck to horizontally span between beams/joists to distribute the horizontal force and design the beams/joists/connections as the compression struts from one side of the building to the other.
This is not an alternative but, rather, a
must when the framing runs perpendicular to the basement walls. In that scenario, the framing braces the concrete slab against buckling. The math on that for buckling will tend to work out nearly identically whether the compressive stress is assumed to exist in the slab, in the framing, or both. In all cases, the lion's share of the stiffness that resists buckling will come from the framing.
Zahait said:
@kootk I don’t think the joists being rigid is really a problem if I count on a k factor of 1.
I disagree and feel that k=1 may be optimistic if one is discounting potential fixity at back spans and wall connections etc which I normally would. If you imagine the meaningful sources of potential misalignment and perturbation for this, that would include:
1) The deflection of the joists.
2) The deflection of the girders supporting the joists.
3) The ponding that you get during concrete pouring that will make the deck non-prismatic and eccentrically loaded.
4) Tolerances in the flatness and levelness of the deck.
Zahait said:
The joists are surely able of supporting this load in the downward direction and I would have to count on the self weight of the slab connection to the deck in the upward direction.
I'm not so sure. Consider:
5) 10 kN/m = 685 plf which is actually a significant load for most steel joists.
6) As with all bracing, it is the stiffness of the bracing that is most important, not the strength. The force requirements specified in CSA are likely assuming that the concrete walls are being braced by wildly stiff concrete slabs such that sufficient stiffness is not in doubt. You're steel joists 'aint that, not by a long shot.