There is another issue: blocking of zero sequence current from the star (Y) side. Probably the CTs delta connected are on the star side of the power transformer.
If you don't do it, the relay may trip unwanted for external faults, necause the delta side of the power transformer blocks zero sequence fault current, but not the star side, so you have to compensate at aux. CT's level.
For numerical relays, this is also done automatically in the algorithm, or it is settable.