111R
Electrical
- May 4, 2012
- 114
What is the typical configuration for the tertiary winding on a Y-Y neutral grounded autotransformer with a delta tertiary?
I've seen cases where:
[ol 1]
[li]The delta is intact internally with two corners tapped and these leads are brought out through bushings. This is used as a power source for station service, etc.[/li]
[li]The delta is open at one corner and these two leads are brought out through bushings. These two bushings are tied together on top and grounded.[/li]
[li]The delta has the configuration of #2, but with another corner also brought out for station service.[/li]
[li]The delta is closed internally and all phases are brought out through bushings for connecting to a reactor or other large load.[/li]
[li]Completely buried[/li]
[/ol]
Does the tertiary need to be grounded on one corner or is it allowed to float with respect to ground?
If station service is not desired, what benefits are gained from being able to break the delta above the tank? Is it mainly for testing or for protection purposes?
Thanks
I've seen cases where:
[ol 1]
[li]The delta is intact internally with two corners tapped and these leads are brought out through bushings. This is used as a power source for station service, etc.[/li]
[li]The delta is open at one corner and these two leads are brought out through bushings. These two bushings are tied together on top and grounded.[/li]
[li]The delta has the configuration of #2, but with another corner also brought out for station service.[/li]
[li]The delta is closed internally and all phases are brought out through bushings for connecting to a reactor or other large load.[/li]
[li]Completely buried[/li]
[/ol]
Does the tertiary need to be grounded on one corner or is it allowed to float with respect to ground?
If station service is not desired, what benefits are gained from being able to break the delta above the tank? Is it mainly for testing or for protection purposes?
Thanks