kalapani
Mechanical
- Mar 11, 2009
- 3
I have Gould end suction SSH pump (4SH2K52B0) pumping water out of cooling tower via 2" piping maybe 2 ft long. On loss of CW make-up and subsequent shutdown air gets introduced into system. Operator start the pump but forgets to bleed air from suction at start-up. This later result is a shutdown somewhere else due to low cooling water flowrate.
I want to make bleeding the air automatic by connecting small diameter tubing from the priming port on the pump casing back to sump of the cooling tower (above water level). Thus hoping there will always be a small amount of water flow in the tubing to purge the air. Has anyone tried this approach and was it successful?
I want to make bleeding the air automatic by connecting small diameter tubing from the priming port on the pump casing back to sump of the cooling tower (above water level). Thus hoping there will always be a small amount of water flow in the tubing to purge the air. Has anyone tried this approach and was it successful?