in Italy the standard connection scheme for HV/MV distribution transformers is Yyn0; there are some thousands of these units, used in primary distribution centres, spanning from 16 to 63 MVA.
The network neutral on the HV side (either 132, 150 or 230 kV) is solidly grounded in power plants and interconnection susbstation, where EHV/HV autotransformers (Yna, 3-limbs without tertiary) are installed, so that there is no need for further grounding the HV network neutral in primary distribution centres.
The medium voltage neutral of HV/MV Yyn transformers is instead grounded at primary distribution centres through a Petersen coil. As the transformers core is always 3-limbs, the zero sequence magnetizing impedance is low enough to allow for the circulation of the zero sequence current when a fault happens on the MV network.
Even in case of long-lasting faults, a proper design of the flux shunts installed on the tank allows for a safe operation of the transformer, without excessive heating of the tank surface. A dedicated type test with neutral current injection (60 s - some 100s of amps) is performed to validate the design.
The main advantage is that the Petersen coil can be directly connected to the star point of the MV winding (no need for a zig-zag neutral grounding transformer). The HV winding can still be designed with a non-uniform insulation as the HV network is solidly grounded.