Engineers,
Someone approached and asked me if is possible to drill a hole (for example 50 ft deep), pour concrete or grout (tremie) but not include any rebars.
I assume this is possible where lateral load is not a concern (only axial capacity is needed).
I guess there is a name for that methodology, can anyone confirm?.
Please let me know. Thanks.
It is absolutely possible. Whether it is appropriate depends entirely on the loads which they must resist. I assume when you say only axial load, you mean only compressive axial load. If that's the case, I would research "rigid inclusions". This would usually fall under the heading of ground improvement rather than deep foundation.
Thanks a lot.
Yes, I meant Compressive axial load only.
I am more familiar with Euro Codes. The reinforcement is a requirement for precast driven piles, and the bored piles subject to tension, bending an shear.
The common practice for the CFA ( continuous flight auger ) piles is , if not necessary the piles without reinforcement can be used and sometimes reinforcement cage provided at only top 4-5 meters .
If the pile will not subject to moment, shear and uplift tension , the answer for bored pile without reinforcement is yes .
Foundations are not the place where I'd want to economise... just like connections.
But there will always be some moment that has to be considered due to eccentricity of axial load.
50 years back, in this area, it was common for small diameter piles to use 4#4 and #3 ties at 3' o/c... I started to use a single #5.
I've also seen where a single bar (perhaps #5 or #6) was placed in the top 10 ft. of the pile and extended out to provide some means of positive attachment to the pile cap or grade beam.
Generally the length of the normal rebar cut in thirds... I just remembered, the bars weren't full length which left the bottom part of the pile unreinforced.