As mpparent notes, the total asymmetrical current is a function of the system X/R ratio at the fault point. The higher the X/R ratio, the greater the possible asymmetry. The asymmetrical current ALWAYS reaches a maximum value in the first half cycle of the fault. This is a transient that damps out after few cycles. In a highly inductive circuit such as a power distribution system (neglecting the loads), the current lags the voltage by nearly 90 degrees. When the fault occurs at a zero voltage crossing, this forces the current waveform to be displaced from the normal balanced waveform. This is essentially a dc transient.
Breakers have a symmetrical rating for fault currents but this is based on a maximum X/R ratio (or power factor) used during breaker testing. If the X/R ratio of your system exceeds the test value, the breaker must be de-rated.
Also, the magnitude of the asymmetrical current also depends on the phase angle of the voltage at the time the fault is initiated. The worst case is when the fault occurs at a voltage zero. If you're lucky, there is no asymmetrical current, but of course, you can't count on this.
dpc