lostinthe triangle -
boffintech's comments are good and seem the be from ACI 530.
There is one pitfall to avoid with reinforced/grouted masonry.
Always base the f'm on the results of a hollow prism and add the appropriate grout AND associated area for the design. Of course, the grout is used to transfer loads from steel to the CMUs, but it also does add to the compressive strength of the wall. The grout should be approximately equal to the net strength of the unit compressive strength of the CMUs or slightly higher. Some codes place a limit on the grout strength, since they can have a higher E, which may distort the stress distribution.
DO NOT fall into the trap of using a grouted prism f'm value that may consist of low strength CMUs filled with high strength grout. This leads to a difference in properties and subjecting the outer fibers in compression to high stresses that may be lower than the interior grout, that do not actually take the load.
It is far more economical to specify a higher block strength (f'm) than to add excessive grout that may not be controlled. - As Jim Amhrein said, "Do not count on what you cannot see", so use quality manufactered materials that can be tested in advance of construction. It is possible to make a 4500 psi prism out of 8500 psi block and 2200 psi mortar. - The problems are finding a use for these high strength masonry assemblages and finding a lab with the machine capacity and platten thickness to do the testing, since most are only set up for 6x12 concrete cylinders.