- Mar 1, 2017
- 51
Hello everyone,
A client wants me to assess an existing structure which is lightly corroded (see attachment). This structure is supporting condensers for a cold storage warehouse building. The structure was built on 2002 and I need to evaluate if it needs an overhaul since one of the old condensers will be replaced by a new one which is around 10% heavier. According to my analyses, little thickness has been lost, and the design is satisfactory (although design factors are near 0.95-1.05), hence I think only a repaint is necessary. Nevertheless, since the design verification is tight, I would like to study further the matter.
So far I have taken a look at ASCE 11 and ASTM G46 only. Is there any other reference you have found useful for this type of work?
Kind regards.
Photos are:
A client wants me to assess an existing structure which is lightly corroded (see attachment). This structure is supporting condensers for a cold storage warehouse building. The structure was built on 2002 and I need to evaluate if it needs an overhaul since one of the old condensers will be replaced by a new one which is around 10% heavier. According to my analyses, little thickness has been lost, and the design is satisfactory (although design factors are near 0.95-1.05), hence I think only a repaint is necessary. Nevertheless, since the design verification is tight, I would like to study further the matter.