WhiteyWhitey
Electrical
- Feb 3, 2009
- 61
Hi All,
During rectification work on the earth grid of a 275kV Underground Cable project the earth grid was damaged by a Jackhammer removing concrete around the copper horizontal conductors.
The critical info is the following.
The earth grid is designed to take any fault curent from the Cable sheath through 4.5kV Surge Arresters to ground. The system is cross bonded and earthed at both ends. this is a dual circuit system. the Cable sheath is designed for 50kA fault Current.
The earth grid has two separate rings in the JB for each circuit that are connected to the link boxes earth point (bottom of surger arresters). Each circuit has 4 x 2m 19mm earth rods connected with 300mm2 stranded copper.
The damage is:
Location 1: Bird Caged conductor with some broken strands. Centre of conductor (copper Clad steel) deformed from impact.
Location 2: Two Broken Strands of the conductor.
My task is to assess the impact this damage will have on the longevity and operation of the earth grid.
My Question is are there any formula or accepted methods to calculate the derating of the earth grid based on the no of strands in the conductor that are damaged?
What is the magnitude of derating from birdcaging of the conductor?
Are there any quick fixes that I have not though out?
The repair of the problem consists of copper wires that are twisted round the conductor to reduce bird caging.
Thanks in advance for any advice.
Your experience is priceless.
During rectification work on the earth grid of a 275kV Underground Cable project the earth grid was damaged by a Jackhammer removing concrete around the copper horizontal conductors.
The critical info is the following.
The earth grid is designed to take any fault curent from the Cable sheath through 4.5kV Surge Arresters to ground. The system is cross bonded and earthed at both ends. this is a dual circuit system. the Cable sheath is designed for 50kA fault Current.
The earth grid has two separate rings in the JB for each circuit that are connected to the link boxes earth point (bottom of surger arresters). Each circuit has 4 x 2m 19mm earth rods connected with 300mm2 stranded copper.
The damage is:
Location 1: Bird Caged conductor with some broken strands. Centre of conductor (copper Clad steel) deformed from impact.
Location 2: Two Broken Strands of the conductor.
My task is to assess the impact this damage will have on the longevity and operation of the earth grid.
My Question is are there any formula or accepted methods to calculate the derating of the earth grid based on the no of strands in the conductor that are damaged?
What is the magnitude of derating from birdcaging of the conductor?
Are there any quick fixes that I have not though out?
The repair of the problem consists of copper wires that are twisted round the conductor to reduce bird caging.
Thanks in advance for any advice.
Your experience is priceless.