The basic question:
You need to check the fasteners for a rainscreen cladding system. You are looking for tension on the fasteners.

From ASCE:
There are two parapet cases for parapets: Case A which applies to the windward side parapet and Case B which applies to the leeward side parapet. Since we are interested in tension on the fastener, we are only concerned with case B.
Case B consists of positive wall pressure on the back parapet "surface" and negative wall pressure on the front "surface".

Discussion:
Looking at the figure it would appear that you really only need to apply P4 which is negative wall pressure from either zone 4 or 5. In this case the force on this fastener would be no different than the wall directly below it.
My argument against this would be - what does ASCE mean as "surface". The parapet as a whole has front and back surface, but so does the piece of cladding. All the elements that make up the parapet have a front and back surface. So should P3 and P4 be applied to the front/back surface of the piece of cladding also? The first logical thought is no, because there is a wall directly behind the piece of cladding. However, there is a gap. Likely the gap is small, but what if it wasn't? At some point it turns into another parapet situation.
Having said this, I don't think this argument holds much weight. If there was no parapet there, you wouldn't be adding any wind pressure to the piece of cladding at the top of the wall. Unless you make the argument that the parapet actually causes an increase in the leeward pressure and that adding P3+P4 is just a numerical simplification. But that is beyond what I'm led to believe per ASCE 7.

Figures:
ASCE_7_Parapet_Cladding_Markup_bhowhx.png

ASCE_Fig_30.6-1_w5spkr.png

ASCE_7_Parapet_Cases_ckeax6.png
 
Replies continue below

Recommended for you

I think your interpretation is correct. The leeward suction for Case B is identical to the leeward pressure on the wall below.

DaveAtkins
 
Like with many particular situations we find ourselves in, the code wasn't written with this in mind. I wouldn't worry about what the ASCE 7 authors intend for your rain screen loads because they didn't have this situation in mind, so you'll have to fill in the gap with your engineering judgement. You have to answer if wind can get behind the rain screen and provide enough pressure to be considered on top of the suction pressure accounted for with p4. I personally would just use p4.
 
In my mind, the correct answer is tied to the method of construction of the parapet. For the vast majority of cases I see, where there are separate planes of cladding on both the inside and outside faces of the structure (often studs), I would agree that correct design suction for fastener design of the outside cladding would be p4. However, I have done some jobs where there really isn't any cladding on the inside face, and the outside cladding receives direct wind pressure on both the front and back faces, and in those cases, I have used p3 + p4. One example that comes to mind is a curtain wall system with glass on the outside face only, that cantilevers up to form the parapet.
 