Jul 16, 2012 #1 efsinc Structural Joined Jun 1, 2008 Messages 68 Location US Would you consider the lateral force Fh (29.5-2) and the uplift force Fv (29.5-3) simultaneous on roof mounted equipment?
Would you consider the lateral force Fh (29.5-2) and the uplift force Fv (29.5-3) simultaneous on roof mounted equipment?
Jul 17, 2012 Thread starter #3 efsinc Structural Joined Jun 1, 2008 Messages 68 Location US The uplift is practically canceling my dead load in my current application. Upvote 0 Downvote
Jul 18, 2012 #4 frv Structural Joined Dec 9, 2007 Messages 996 Location US Yes. It will do that. Strap it down. Upvote 0 Downvote