ASCE 7-10 Wind load on external stair
designforce
Hi all,
I have an external stair, wood framed, going up the side of a single family house from 1st to 2nd floor. Just wood stringers and tread/risers. Risers are closed. I can't figure out which section of ASCE applies. None of the classifications in the component and cladding section really applies, I think. Roof overhang is way conservative for something like this, plus, the roof is 2 floors up. Non-building/appurtenance doesn't give me uplift, which I think is absolutely needed.
I can take CC and go, to be conservative, but the thing will look ridiculous! What would you recommend?
You are correct, your roof would seem to be too high to have any effect on the wind pressure for the external stair.
I believe Component and Cladding is the way to go here, and I would use the same pressure as the surrounding walls, but applied normal
to the underside of the stair. The idea being if the wind is acting like a fluid, you'd have the same fluid pressure as the walls.
If you look at Figure 30.7-2 in ASCE 7-10 this idea is supported. The figure shows how the roof overhang C&C loads are determined, but
in your case you wouldn't have the p(ovh) load, only the p(s) which is equal to the p(w), the C&C load on adjacent walls.
CF