- Jan 28, 2008
- 26
I have a discussion with my coworker about footing design subjected to vertical forces due to D, L, and E loads. The soil report permits a 1/3 increase in allowable soil stress for transient load conditions.
I say the following points,
1. To get the max expected soil compression stress and the required footing horizontal dimensions, it is better to use the ASD combination in ASCE-05, (D+0.75x0.7E +0.75L), where E=Eh+Ev (E is reduced by 25% according to ASCE-05 item 12.13.4).
2. To get the max expected soil tension stress, it is better to use the ASD combination in ASCE-05, (0.6D+0.7E), where E=Eh (E is reduced by 25% according to ASCE-05 item 12.13.4 and Ev=0 according to ASCE-05 item 12.4.2.2 exception 2).
3. To design the footing (depth & reinforcement) it is better to use strength design combination in ASCE-05, (1.2D+0.5L+E), where E=Eh+Ev (No reduction for E by 25% according to ASCE-05 item 12.13.4).
4. To check the soil bearing capacity we should follow the soil report in permitting a 1/3 increase in allowable soil stress for transient load conditions
My coworker says,
• In point No.1 we should not use E=Eh+Ev but we should use E=Eh because ASCE-05 item 12.4.2.2 exception 2 tells in determining demands on the soil-structure interface of foundations Ev should be zero.
• In point No.4 no increase in allowable soil stress for transient load conditions according to IBC-2006 item 1605.3.1.1.
Any one can give professional comments about my three assumptions as well as my friend point of view?
I say the following points,
1. To get the max expected soil compression stress and the required footing horizontal dimensions, it is better to use the ASD combination in ASCE-05, (D+0.75x0.7E +0.75L), where E=Eh+Ev (E is reduced by 25% according to ASCE-05 item 12.13.4).
2. To get the max expected soil tension stress, it is better to use the ASD combination in ASCE-05, (0.6D+0.7E), where E=Eh (E is reduced by 25% according to ASCE-05 item 12.13.4 and Ev=0 according to ASCE-05 item 12.4.2.2 exception 2).
3. To design the footing (depth & reinforcement) it is better to use strength design combination in ASCE-05, (1.2D+0.5L+E), where E=Eh+Ev (No reduction for E by 25% according to ASCE-05 item 12.13.4).
4. To check the soil bearing capacity we should follow the soil report in permitting a 1/3 increase in allowable soil stress for transient load conditions
My coworker says,
• In point No.1 we should not use E=Eh+Ev but we should use E=Eh because ASCE-05 item 12.4.2.2 exception 2 tells in determining demands on the soil-structure interface of foundations Ev should be zero.
• In point No.4 no increase in allowable soil stress for transient load conditions according to IBC-2006 item 1605.3.1.1.
Any one can give professional comments about my three assumptions as well as my friend point of view?