AS3851 Unable to calculate X/R ratio

Status
Not open for further replies.

silkwormfrog

Electrical
Apr 27, 2013
3
Hi

I have trying to calculate the fault level (ground fault) by using AS3851 method.

In section 8.5.2.1, the factor k for the R/X and X/R ratios can be obtained using
k = 1.02 + 0.98 * e ^(-3R/X).

I have been given the following:
the source 3 phase max. fault level 3800A
the source 3 phase max. fault level 3600A

the source 1 phase max. fault level 930A.
the source 1 phase max. fault level 910A

So for 3 phase fault, k = 0.746.
The problem is I cannot obtain R/X ratio using k = 1.02 + 0.98 * e ^(-3R/X) due to obvious reasons.

Is there anyway to get around this problem. Please note I need to follow AS3851 standard. Many thanks

 
Replies continue below

Recommended for you

Could it be that you have got it the wrong way around? k is needed for the peak current of 3-phase fault. k is calculated using the equation you refer to. You need R/X for k. In IEC-world the corresponding standard gives three ways to calculate R/X. I guess the same applies to AS-world. In addition k = 0.746 does not look correct.
 
Reading between the lines - are you saying the peak (Ip) current is 3800A and rms current (Ik") is 3600A? If so, that peak current is way too low. I think it is probably out by a factor of sqrt(2). If so, the real peak current would be 5374A and X/R would be 4.11.

This is close to what would be expected as an X/R ratio at a final distribution transformer (0.4kV), although those currents look a bit low for that.
 
Thanks for the comments.

The fault level is given by the supply authority. And this is a 22kV distribution network.
 
What are those fault levels supposed to mean?

Is the first one the peak?

I really don't understand what you're asking. Section 8.5 of AS3851 is written so you can work out the peak current (ip).
 
Utility max and min source positive, negative, zero sequence impedances are required to determine the Utility contribution to a short-circuit at the Utility connection.
If the Utility only provides short-circuit current contribution, then the following is required:
- Max and Min PPP and PE short-circuit contributions from the Utility ( preferably in amps ),
- X/R for PPP = X1/R1,
- X/R for PE = X1+X2+Xo / R1+R2+Ro.
- Was the Utility contribution calculated using the voltage 'c' Factor ?


 