Here's something that just tripped me up.
P=1/800 kp=1.25
P=1/500 kp=1.0 (BCA Importance Level 2)
P=1/250 kp=0.75 (nominal design life of 25 years)
Unfortunately there is no commentary on this which leaves me thinking that the value in 4.6.2.1 General is a mistake.
I'd appreciate any clarification.
AS2304:2019 - 4.1
The design life of water tanks for fire protection systems for the determination of design actions within this Section shall be a minimum of 25 years and a minimum importance level of 2 as specified in AS/NZS 1170.0
However if you go to AS 1170.4, Table 3.1 you findAS2304:2019 - 4.6.2.1 General
Kp = probability factor for earthquake from AS 1170.4, Table 3.1
The value of Kp for fire tanks shall be 1.25
P=1/800 kp=1.25
P=1/500 kp=1.0 (BCA Importance Level 2)
P=1/250 kp=0.75 (nominal design life of 25 years)
Unfortunately there is no commentary on this which leaves me thinking that the value in 4.6.2.1 General is a mistake.
I'd appreciate any clarification.