Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

AS1418.18

Status
Not open for further replies.

Mb87

Industrial
Joined
May 15, 2023
Messages
7
Location
AU
Got a small project for some crane runways.
common design. portals, with a UB on corbels.

Just doing all the design checks and I have come to a halt at vertical web loads.

aaa_a2k4ny.png

Most of this is pretty straight forward except for a factored bending moment.
There is no real mention of this can I just use Nw*Ey (as per clause 5.3.2)
where Nw is factored wheel load and an Ey is the lateral design eccentricity?
 
Here you are assessing the interaction of global bending and local transverse [bearing] loads at the top of the web, not torsional loading. This should be your in-plane bending moment on the runway girder. I think it is misleading where they reference Figure 5.7.3.2, since this is really applicable to clause 5.7.3.4 IMO.
 
Thanks for the reply BJI
While were looking at this case, the standard has no actual reference for unstiffened webs all Web buckling relies on patch loading based on stiffener spacings.
Tips?
 
If you are going to stick with limit state design, then refer back to AS4100 CL5.13.
 
Status
Not open for further replies.

Similar threads

Part and Inventory Search

Sponsor

Back
Top