Hi,
A building has both normal and 100% back-up generator power supplies. There is a service protection device on the normal side and a circuit breaker on the generator side. These breakers are connected to the busbars via one automatic transfer switch.
The question is:
Can this transfer switch then have connected after it (on the load side) the outgoing submains to fire and life safety items?
This (first) option seems to be compliant with the exception number (vi) of Section 7.2.2.3 of AS 3000 and is more resonable and cost effective. My understanding is that this clause is a waiver of the below.
Or is a second separate automatic transfer switch required to seaprate these items from the remaining items (power and lighitng), so that a single switch does not switch at the same time normal and safety services?
This second interpretation is more expensive and strict implementation of Section 7.2.2.1 of AS 3000.
Any votes?
Thanks.
A building has both normal and 100% back-up generator power supplies. There is a service protection device on the normal side and a circuit breaker on the generator side. These breakers are connected to the busbars via one automatic transfer switch.
The question is:
Can this transfer switch then have connected after it (on the load side) the outgoing submains to fire and life safety items?
This (first) option seems to be compliant with the exception number (vi) of Section 7.2.2.3 of AS 3000 and is more resonable and cost effective. My understanding is that this clause is a waiver of the below.
Or is a second separate automatic transfer switch required to seaprate these items from the remaining items (power and lighitng), so that a single switch does not switch at the same time normal and safety services?
This second interpretation is more expensive and strict implementation of Section 7.2.2.1 of AS 3000.
Any votes?
Thanks.