IEEE C62.22 recommends that for a delta connected primary you configure 3 arrestors in a wye configuration (rated at line to neutral voltage) with a fourth arrestor connecting these three to ground. Ref IEEE C62.22 Figure Eight on Page 28 (Sect 5.5.4.2).
Does anyone have any physical drawings showing this applied for a 230kV primary (utilizing 144kV MCOV arrestors)? The height of the arrestors and/or insulator requirements appears to preclude us from applying directly at the transformer, and a horizontal arrangement may be difficult with the fourth arrestor.
Does anyone have any physical drawings showing this applied for a 230kV primary (utilizing 144kV MCOV arrestors)? The height of the arrestors and/or insulator requirements appears to preclude us from applying directly at the transformer, and a horizontal arrangement may be difficult with the fourth arrestor.